The National Electrical Manufacturers’ Association (NEMA) issues guidelines and ratings for an enclosure’s level of protection against contaminants that might come in contact with its enclosed equipment.

There are many numerical NEMA designations; we’ll discuss NEMA enclosures relevant to our on-line catalog: NEMA 3, NEMA 3R, NEMA 4, NEMA 4X, and NEMA 12.

NEMA 3 enclosures, designed for both indoor and outdoor use, provide protection against falling dirt, windblown dust, rain, sleet, and snow, as well as ice formation.

The NEMA 3R rating is identical to NEMA 3 except that it doesn’t specify protection against windblown dust.

NEMA 4 and 4X enclosures, also designed for indoor and outdoor use, protect against windblown dust and rain, splashing and hose-directed water, and ice formation. NEMA 4X goes further than NEMA 4, specifying that the enclosure will also protect against corrosion caused by the elements.

NEMA 12 enclosures are constructed for indoor use only and are designed to provide protection against falling dirt, circulating dust, lint, fibers, and dripping or splashing noncorrosive liquids. Protection against oil and coolant seepage is also a prerequisite for NEMA 12 designation.

 

Additional resources:

How NEMA standards are developed

How to read a NEMA standard

0

Networking equipment—especially servers—generates a lot of heat in a relatively small area. Today’s servers are smaller and have faster CPUs than ever. Because most of the power used by these devices is dissipated into the air as heat, they can really strain the cooling capacity of your data center. The components housed in a medium-sized data center can easily generate enough heat to heat a house in the dead of winter!

 

So cool you must, because when network components become hot, they’re prone to failure and a shortened lifespan. Damage caused by heat is not always immediately evident as a catastrophic meltdown—signs of heat damage include node crashes and hardware failures that can happen over a period of weeks or even moths, leading to chronic downtime.

 

It’s also important to ensure that individual cabinets used for network equipment provide adequate ventilation. The temperature inside a cabinet is affected by many variables, including door perforations, cabinet size, and the types of components housed within the cabinet.

 

The most direct way to cool network equipment is to ensure adequate airflow. The goal is that every server, every router, every switch has the necessary amount of air no matter how high or low it is in the cabinet. It takes a certain volume of air to cool a device to within its ideal temperature range. Equipment manufacturers provide very little guidance about how to do this; however, there are some very basic methods you can use to maximize the ventilation within your cabinets.

 

Open it up

Most major sever manufactures recommend that the front and back cabinet doors have at least 63% open area for airflow. You can achieve this by either removing cabinet doors altogether or by buying cabinets that have perforated doors. Because most servers, as well as other network devices, are equipped with internal fans, open or perforated doors may be the only ventilation you need as long as your data center has enough air-conditioning to dissipate the heat load. You may also want to choose cabinets with side panels to keep the air within each cabinet from mixing with hot air from an adjacent cabinet.

 

Equipment placement

Don’t overload the cabinet by trying to fit in too many servers—75% to 80% of capacity is about right. Maintain at least a 1.5” clearance between equipment and the front and back of the cabinet. And finally, ensure all unused rack space is closed off with blank panels to prevent mixing of hot and cold air.

 

Fans and fan placement

You can increase ventilation even more by installing fans to actively circulate air through cabinets. The most common cabinet fans are top-mounted fan panels that pull air from the bottom of the cabinet or through the doors. For spot cooling, use a fan or fan panel that mounts inside the cabinet.

 

For very tightly packed cabinets, chose an enclosure blower—a specialized high speed fan that mounts in the bottom of the cabinet to pull a column of cool air from the floor across the front of your servers or other equipment. An enclosure blower requires a solid or partially vented front door with adequate space—usually at least 4 inches—between the front of your equipment and the cabinet door for air movement.

 

When using fans to cool a cabinet, keep in mind that cooling the outside of a component doesn’t necessarily cool its inside. The idea is to be sure that the air circulates where your equipment’s air intake is. Also, beware of installing fans within the cabinets that work against the small fans in your equipment and overwhelm them.

 

Air conditioning

Air-conditioned cabinets keep equipment cool and save energy because you cool just the cabinet and not the entire room or IT center. ClimateCab models are perfect for harsh environments and remote locations without cooling infrastructures.

 

Temperature monitoring

To ensure that your components are operating within their approved temperature range, it’s important to monitor conditions within your cabinets. The most direct method is to put a thermometer into your cabinet and check it regularly. This simple and inexpensive method can work well for small installations, but it does have its drawbacks—a cabinet thermometer can’t tell you what the temperature inside individual components is, it can’t raise the alarm if the temperature goes out of range, and it must be checked manually.

 

Another simple and inexpensive addition to a cabinet is a thermostat that automatically turns on a fan when the cabinet’s temperature exceeds a predetermined limit.

 

Many network devices come with SNMP or IP-addressable internal temperature sensors to tell you what the internal temperature of the component is. And, there are also cabinet temperature sensors that can alert you over your network.

 

The AlertWerks Environmental Monitor System not only monitors temperature within a cabinet, but also humidity, the presence of water or smoke, airflow, and security as well.

 

It’s easy!

Keeping your data and server cabinets cool doesn’t have to be complicated. Just remember not to overcrowd the cabinets, be sure to provide adequate ventilation, and always monitor conditions within your cabinets.

0

Given the heat wave so much of the country is experiencing (deepest sympathy to those readers in Richmond, VA that may experience a heat index of 118 degrees today); we had an itch to talk about cooling. That is, cooling in the data center.

 

Did you know that legacy data centers waste at least 50% of the energy they consume managing heat generated by IT systems? Most data centers are not new; they are housed in buildings that are using practices that could be 20 years old and have not yet caught up with the latest trends.

Fully populated racks can dissipate as much as 7–25 kW of heat per rack. High-end servers can dissipate more than 40 kW per rack. This level of density requires data centers to provide power and cooling densities that exceed typical current capabilities.

Furthermore, most legacy data centers have not been designed to use their maximum capabilities, best practices have not been implemented, and the cooling methods of IT equipment have been considerably less than optimal. This has created a common situation, as identified by the Uptime Institute, where data centers consume 2.0 to 2.6 times the cooling required by the IT equipment, thus wasting energy and power and further reducing the amount of IT that can be housed in the structure.

By implementing best practices and optimizing the performance of the existing air cooling infrastructure, data center operators can improve the performance of the specified cooling infrastructure to 70% efficiency. The question data center owners must ask themselves is if their current air cooling is acceptable at 70% or if they can continue to sustain that performance as computing technologies push power and cooling beyond their current requirements.

What can operators expect from their environment if cooling requirements exceed 12 kW to up to 25 kW per rack? Read our entire Extending the Life of Your Data Center white paper. Or, check out our storage technologies to help keep IT equipment cool and to cut rack power and cooling costs by as much as 50%. Nothing cools like chilled water!

 

Did you know you can reduce your utility bills in other ways, too? Eight ways to reduce power consumption.

0

Once you’ve chosen your cabinet, whether it be customized Elite or an energy-saving ClimateCab, it’s time to add accessories for even more function.

 

Cabinets have two sets of rails, front and back, where you can mount shelves, trays, cable managers, and power strips.

 

Shelves

Cabinet shelves are an easy solution for storing things that aren’t rackmountable. The shelves attach to the rails; servers or other equipment sits on the shelves. Make sure the shelf has the weight capacity you need—some can hold hundreds of pounds. For easy access to components in your cabinet, choose a sliding shelf. There are also vented shelves that improve air circulation within the cabinet.

 

Although most shelves fit 19” rails, there are shelves that go on the less-common 23” rails. There are also brackets that can adapt many devices intended for 19” mount to 23” rails.

 

Keyboard Trays

Keyboard trays are space-saving solutions that also keep your data center organized. They slide neatly into your cabinet or rack—and out of your way—when not in use. And they usually fit into only 1U of rack space.

 

KVM Trays

Further reduce clutter in your server room by using KVM trays that are 1-or 2U high mounted in your cabinet. Special features of many KVM trays include rock-solid construction, LEDs on the front panel for easy location in a darkened data center, and integrated KVM switching.

 

Front-panel controls enable you to use the buttons on a monitor bezel without pulling out the keyboard. Some trays have USB ports for access.

 

Cable Managers

Cabinets usually have built-in troughs for cable routing, knockouts for cable pass-throughs, and tie-off points for cable management. You can also add horizontal or vertical cable managers to the cabinet’s rails to manage and route cables more efficiently. Cable managers control bend radius to protect cables from hidden crushes, inks, and snags, and reduce maintenance time by keeping your cabinet neat and organized. Plus, properly managed cables help to improve airflow.

 

SpaceGAIN

If you have no room to spare in your cabinet, think SpaceGAIN. You might not think of a patch panel as an “accessory,” but SpaceGAIN angled-port and angled path panels are not your average panels. They free up valuable space and eliminate the need for horizontal cable managers. You save time and money by routing cables directly into ports. And SpaceGAIN high-density feed-through patch panels enable you to fit 48 ports into only 1U of rack space, with no punchdowns needed.

 

To save even more space, use SpaceGAIN 90° Right-Angle CAT5e/CAT6 cables. Their up, down, left, or right angles save up to 4” of space in crowded cabinets.

 

PDUs and UPSs

Control the distribution of power in your cabinet with a power distribution unit. A PDU can be basic or “intelligent,” with surge protection, remote management, or power and environmental monitoring. Integrate a PDU directly into an uninterruptible power supply (UPS) for extra reliability.

 

Security

Most cabinets come with a lock and key, but more advanced options are available to provide a higher level of security. Keyless options include combination locks and biometric locks that read fingerprints.

 

Fans and Blowers

Ventilation in your cabinets is critical for keeping vital equipment cool.

 

An enclosure blower draws cool air from a raised floor at the bottom of the cabinet and delivers it right across the front of servers or other network components. It fits on standard 19” rails and uses only 2U of mounting space. This high level of ventilation lowers the temperature of cabinet hot spots by up to 15° F. Lowering temperature protects your electronics against failure caused by overheating, which may enable you to install more equipment.

 

Fan panels or fan trays direct maximum airflow with very little noise to heat-sensitive rackmounted equipment. Position them in your cabinet wherever you need them the most.

 

Most network devices take in air through their front panels and expel it out the back. Filler panels in unused rack spaces help keep cool air in the front of the cabinet where it can be used by the equipment.

 

For more information on effective cooling techniques, read our blog post on efficient cooling in the data center.

0

Although it might seem like air conditioners produce cold air, they actually work by removing hot air from the cabinet and transferring the heat away from the cabinet itself. The air flowing back into the enclosure has the heat removed and thus feels colder.

 

Air conditioners designed for cooling electronics have two basic systems at work within them: The first is the compressor, refrigerant, evaporator coil, and condenser coil system, which transfers the heat from inside the cabinet to outside the enclosure. The second is the air mover system, which is comprised of a cabinet-side blower and exterior-side blower. The cabinet side blower circulates the hot enclosure air over the evaporation coil, so that the refrigerant can pick up the heat energy and move it to the exterior of the air conditioner. The exterior-side blower then exhausts the heat away from the condenser coil to the outside of the air conditioner.

 

Unlike domestic building cooling, where the evaporator coil and blower are separate from the condenser coil, compressor, and condenser blower, systems designed for electronics cooling usually package these components together in one unit. Because electronics cooling is not designed for human comfort, the thermostat is typically not set any lower than 75° F (23.8° C). This higher temperature range reduces the chance of condensation forming inside the enclosure or on vital electronic equipment.

 

BB-enclosure-airflow.jpg

0

Configurators and Selectors are interactive tools that make it even easier for you to get the solutions you need. Whether it’s cables, cabinets, or KVM, we provide simple to use guides that help make your decisions a snap.

CATx Cable Selector
Quickly find the exact CAT5/5e/6/6a/7 cable you need.

Custom Cable and Adapter Configurator
Design your custom cable or adapter and submit your request to our engineers for review. A Black Box representative will contact you, typically in 24 hours or less, to confirm your order.

KVM Switch Selector
Find the perfect ServSwitch™ KVM solution for your application.

Cabinet Configurator
Twenty seconds to configure, two days to ship. Build your ideal cabinet, configured to your specs and shipped in two business days.

Wallmount Cabinet Selector
Select wallmount features in the order of your priorities and get a list of matching cabinets.

0

Cooling in the data center can be a  lot like a black money hole, in that it’s a big energy sucker. How can  you keep it cool and balance your budget by using efficient cooling  technology? We know that the growing demand for power is a challenge, so  choosing the best system for your data center is important.

 

Fortunately,  there are a number of cooling methods to choose from, whether you are  building a new data center or retrofitting one. And emerging green  technologies offer exciting possibilities for advances in efficiency and  cost savings.

 

Whether  under the floor, above the floor, in the rack, or above the rack, the  requirement of data center cooling remains the same: Warm air must be  moved away from equipment and cool air towards it. Understanding the  factors that can hinder or even prevent this from happening is one of  the first steps to improving data center efficiency.

 

Air conditioners and air handlers
The familiar air conditioner (AC) unit, installed in the data center  and connected to outside condensing units, uses a fan system to move  cool and hot air where they need to be. It’s much like the systems used  in residential settings except that, in building, cooling, the  evaporator coil and blower are separate from the condenser coil,  compressor, and condenser blower, while in electronics cooling they are  packaged together in one unit.

 

Computer  room air handlers (CRAH) work much the same way except that they use  chilled water instead of refrigerant to remove heat from the air.

 

You might think that the drier the data center, the better. But, in fact, the American Society of Heating, Refrigerating, and Air-Conditioning Engineers (ASHRAE) has a recommended range of humidity levels to help ensure longevity.

 

Hot aisle/cold aisle
The idea of hot aisle/cold aisle seems simple, but it’s a little  tricky. Ideally, cool air passes in front of parallel rows of racks,  being drawn in toward equipment, and hot air comes out the back of the  rack or overhead and is exhausted out of the room, producing constant  air circulation.

 

Most  major server manufacturers recommend that cabinet doors used in hot  aisle/cold aisle installations have at least 63% open area for airflow.  You can achieve this by either removing cabinet doors altogether or by  buying cabinets that have mesh doors. Also, cabinets with side panels  keep the air within each cabinet from mixing with hot air from an  adjacent cabinet.

 

Because  most servers and other network devices are equipped with internal fans,  open or mesh doors may be the only ventilation you need as long as your  data center has enough air-conditioning to dissipate the heat load.

 

Here’s  where the tricky part comes in. Cool air can escape through various  holes like cable cutouts, and some hot air doesn’t get exhausted and may  enter the cold aisle, resulting in inefficient air handling and the  presence of hot spots. These problems can be overcome through various  analyses and equipment modifications.

 

Blanking panels,  for example, can prevent cold air from passing through a cabinet too  quickly or in the wrong direction and are a simple and economical way to  direct cold air through equipment and prevent it from mixing with hot  air. Brush strips, although not airtight, can cut down on air leakage while keeping dust and other contaminants out of cabinets.

 

You can increase ventilation by installing fans to actively circulate air through cabinets. The most common cabinet fans are top-mounted fan panels that pull air from the bottom of the cabinet or through the doors. Or  you can use a fan or fan panel that mounts inside the cabinet or choose  cabinet doors with built-in fans. For very tightly packed cabinets, an enclosure blower is a specialized high-speed fan that mounts in the bottom of the  cabinet to pull cool air from a raised floor across the front of the  cabinet where it can be used by equipment. An enclosure blower requires a  solid front door with adequate space—usually at least four  inches—between the front of your equipment and the cabinet door for air  movement. If you’re housing components outside of a  temperature-controlled area, you may want a cabinet with its own air conditioner.

 

Hot aisle/cold aisle containment
In hot aisle/cold aisle containment,  barriers are used to enclose the aisles, ensuring cold air and hot air  stay where they should be to maximize AC efficiency. Cold air stays near  the server intake, and hot air exhaust is shuttled to in-row air  conditioners, conditioned, and then returned to the cold aisle.

 

To  keep cool air from mixing with arm air, row ends are closed off with an  airflow barrier. This barrier can range from makeshift arrangements of  plastic strips to doors made specifically for this purpose.

 

Because  cold aisle containment concentrates cool air at the front of equipment  where it’s most needed, it’s a great cooling method. Cold aisle  containment significantly reduces energy costs, lowering power bills as  well as reducing data centers’ carbon footprints.

 

http://bboxblog.files.wordpress.com/2011/04/hotaisle-coldaisle.jpg

Liquid cooling
Liquid cooling systems are air conditioners that use a liquid to dissipate heat. That  may be cold water or refrigerant, but the difference is that the liquid  is closer to the heat source, resulting in even more efficient cooling.

 

Green cooling
The world of data center cooling is evolving alongside “green” or  sustainable technologies, as data center managers contend with power,  cooling, and space limitations.

 

Servers  designed to handle higher temperatures are an example of so-called  “adaptive” cooling. “Free” cooling, on the other hand, is almost like  simply opening a data center window, except the windows are filters and  louvers for cleanliness and air control. In the right environment,  methods such as these can save tremendous amounts of money and energy.

 

Geothermal  cooling is an example of a more involved green system. In traditional  chilled water system, a majority of the water can be lost to  evaporation. With geothermal cooling, evaporation can be cut to zero.

 

Power demands generally vary throughout the day, and system with variably frequency drives can adjust the power as needed.

 

Chill out!
These and other evolving technologies may drastically change the way  data centers are cooled in the future. Choosing the right cooling system  saves money and protects your investment. How do you keep your data  center cool? What advice would you offer to others looking to build or  retrofit their data center?

 

Data center resources:
Quiet Fan Panels: Equipment cooling without the noise (PDF)
Video: How to pick a cabinet
White Paper: Extending the Life of Your Data Center