During my review of the Megger  MIT420/2 insulation tester in Blog 9, I tested a 120MW Generator rotor winding that actually failed the insulation resistance test. Following this issue, the bedplate heaters for the generator were reconnected and placed back into service. Around 4 weeks later, I returned to the generator to carry out a further insulation test with the expectation that the heat would have driven out the moisture from the winding and a healthy insulation reading would be obtai ...